Forum Discussion
BFL13
May 20, 2022Explorer II
Long thin wire to the furnace means a voltage drop. So if the furnace needs X volts to run right, your batts have to be above that by at least that voltage drop, so that can mean you can't do it when the batts get low and then the voltage drop takes the voltage to the furnace too low.
Cure is change to fatter wire or a higher AH battery bank or to a battery type with higher voltage per SOC.
You can also put your meter at various points along the furnace parts to see if there is a big drop that should not be there from one part to another. I had that and found a wire was not tight on one of the spade terminals so the next part had its voltage too low.
Cure is change to fatter wire or a higher AH battery bank or to a battery type with higher voltage per SOC.
You can also put your meter at various points along the furnace parts to see if there is a big drop that should not be there from one part to another. I had that and found a wire was not tight on one of the spade terminals so the next part had its voltage too low.