If you are getting 120V from EACH hot leg to neutral, then you do not have a tripped breaker.
The only way to get zero between the two hots is for "someone" to have changed the wiring, either back at the panel or in the receptacle itself.
You need to trace it back to ensure you do in fact have two separate hot feeds, one from each half of the 240V service to the house.
The only way to get zero between the two hots is for "someone" to have changed the wiring, either back at the panel or in the receptacle itself.
You need to trace it back to ensure you do in fact have two separate hot feeds, one from each half of the 240V service to the house.