Fisherguy
Jan 26, 2023Explorer
waexplorer wrote:
Ok Fisherguy, from an earlier post I saw you have volt/amp guage. If you can run your batteries down 30-50% SOC then you can monitor recharge amps and volts. IF your charger is charging at 14.4-14.6 volts with 50-60 amps, more than likely that's a lithium profile. IF your readings are more like 13.6-13.8 with lower amps, that's a FLA curve. Some Flooded curves will start over 14 volts and drop after an hour or so. Lithium will hold over 14 volts for as long as it takes to recover SOC. Depending on how many amp hours it needs to put back in the batteries. Most lithium battery makers use prismatic cells @3.2 volts. 3.2x4=12.8 volts. MAX charge per cell is 3.65 and 3.65x4=14.6. Lithium charge curves stay flat for most of the charge cycly then ramp up voltage sharply at the end. This is not charging voltage, this is state of charge voltage. The BMS is should be a 50 or 100 amp which is what charge/discharge current you can run through it. I wouldn't replace anything until you have an idea of your WFCO charge curves/amps etc. Run through a few charge/discharge cycles and see if you actually need more than what's there. And you can also do this using the Honda generator as well. Also as the batteries get closer to 100% SOC the charging amps will drop. Aso, the batteries BMS will stop the charge cycle when the batteries are full and cell balancing will begin. Lithium battery cells don't like too much variation between cells.
Thanks.
Plugged it in with batteries at 46%, got 27.5 amps at 13.6 volts.
I've since heard back from WFCO who told me the previous owner didn't install the 12V circuit board that has the 'lithium switch' on it so I won't get 14.6V. They offered to sell me the DC board.
Having RV issues? Connect with others who have been in your shoes.24,329 PostsLatest Activity: Oct 27, 2025
