j-d wrote:
Their model designations are confusing, but it sounds like our Mach 15, except you have three fan speeds and we have only two.
Yes the compressor will get HOT. Blower motor too, actually.
When you hear it "kick on" can you tell if it's actually spinning up, or if it's sitting in a "locked rotor" state? The trick is that it'll look like Locked if the Start Device and/or Running Capacitor has failed. It could also be spinning up but not providing cooling because
1. Refrigerant Leaked Out
2. Internal Compressor Failure
Either would mean Problem in Sealed System which = Replace A/C
But! Still a very good chance of things like defective capacitor(s). Our Coleman has a Fan Run Capacitor, and yours is clearly Good. Then it has a Compressor Run Capacitor (suspect in this case), AND some kind of Start Device. On ours, Start consists of a Capacitor AND a cut-out device. Ours is a Relay. Others could have a PTCR device.
I wish we were camped together. With my Meter, Clamp-On Ammeter, and the spare capacitors I carry along, could tell you real quick whether you should replace or not.
WHOA! WAIT! You can test your bad unit by Substitution! Swap the suspect parts with same from your working A/C! With POWER OFF, take a photo of the wiring (aid in reassembly), short the Capacitors across the terminals (might be holding a charge) then disconnect, remove, and switch the Compressor Start and Run devices to the non-working unit. Power it up and see if it starts. If it does, you can get fancy and try to tell if it's Start or Run that's bad, but you can buy both for around $30 from Amazon, eBay, etc. Capacitor will be marked with its microfarad rating, probably 40mfd at 370VAC, and a SUPCO SPP6E Start Device will replace both the Start Capacitor AND its Relay or PTCR device.
Good post and advice. Also the clamp on amp meter is a good investment. Make sure it is one of the new ones that reads both AC and DC.