I am getting ready to start the inverter project and the breaker box in the FW has Murray MH-T breakers what is compatible to put in there? Need a 30 amp single pole.
kellertx5er wrote:That relates to a Solar Grid Tie inverter that shuts down when utility power is not present.
" its against code and dangerous to back feed the main panel from the inverter"
NEC Article 690 specifically ALLOWS an inverter to backfeed into the service panel (690.10(C)).
" use dedicated NEW circuits for inverter output"
That's exactly what the OP is proposing to do.
If equipment is properly labeled to indicate multiple power sources, this arrangement is acceptable.