time2roll wrote:
Not really separate as there is a common Hot(2), Neutral and Ground to feed the string or row in the campground.
So you will have a common Neutral Bus and Ground Bus where all are connected.
The main hots will feed the breaker bus.
There are not separate wires for each connection going back to the main panel.
That makes sense. I recall reading some time ago that "properly wired" campground pedestals will have two service feeds, one dedicated to the 50A and another to the 20A/30A breakers. However, I can easily see where most installers wouldn't do that unless the code specifically required it. In the case of this pedestal, the breakers do all appear to be on the same bus.
Knowing that, I'm still trying to figure out why the GFCI (or potentially the 30A breaker) would (or could) cause an open ground situation leading to the hot skin, and why that wouldn't show up when testing the grounds.
Am I misunderstanding something?