enblethen wrote:
60 amp would be rating. You could drop down to fifty as most rigs do not use the full 60 amp.
Circuit should be 120/240 four wire. two 120 volt legs with 240 across them, one neutral and one ground.
The panel also has a GFCI duplex 15/20 amp outlet on it's own breaker. A 60 amp breaker would allow about 80% of the maximum possible load before tripping.