ScottG wrote:Dutch_12078 wrote:
60 amp 240 from a 60 amp double breaker in your main panel... You'll need to run a 4-wire (3 plus ground) 6GA copper line at a minimum, 4 GA if the run is very long. If you run aluminum, use 4GA instead of 6GA. Make sure the neutral and ground are NOT bonded at the sub-panel.
Best answer.
This is what I was looking for!
Thanks!!