SiO2 Batteries and High Amp Draws

SiO2 is a specialty battery type that most folks would have no use for vs the usual RV battery types. They cost a lot too.( I had a special reason to get one)

Here is some info on them --I am not selling them!!! Just trying to show what they are

https://azimuthsolar.ca/product/12v-100ah-sio2-battery/

One big thing they are supposed to be good for is high amp draw loads for their size in AH. So here is what I found on that:

1. The 200AH bank (two 100s) with the 2000w MSW inverter and my wiring job has a voltage drop that stays about the same for the same load at any SOC above inverter shut-off voltage.

2. The MW draws about 55 amps and the kettle draws about 89 amps and the furnace in the TC draws about 3.5 amps.

So example using kettle to boil water for cup of instant coffee. (No advice needed on making coffee, you latte bunch, thanks anyway :) )

A. Monitor before start--142AH, 12.7 volts, 71% SOC
After start- 88.7 amps draw, 11.7 volts, about five minutes kettle off
Monitor now--135AH, 12.5 volts (rising slowly), 68%

So that time 89/142 is a 63% draw.

B. Before-- 113AH, 12.3 volts, 57%
-11.5v at 88a
-11.2v at 90.5a
-11.1v at 90.6a
After= 106AH, 53% SOC

So that time 90/110 is an 82% draw.

(note how inverter amps go up as voltage goes down--"inverter creep" The inverter did not alarm at the 11.1 but would have at 11 but still run until shut off at 10 something. Both times cost about 7AH each

C. Another example kettle and furnace on 107AH and now 90.1 amp draw voltage 10.9 and inverter beeping

So that time 90/107 is an 84% draw.

I first got one SiO2 to run the MW (700w RCA) in the TC and did a quick test where ISTR it ran its 55 amp draw for over 30 minutes till SOC was about 20% afterwards. The battery discharge tables in their specs showed the discharge time was close to specs for that size draw.

The comical thing is I learned the MW can heat the water enough to make my coffee using fewer AH than the kettle in the TC.
-kettle 5 minutes at 89 amps --voltage drop 1.0 volt
-MW 3 minutes at 55 amps (MSW inverter. A PSW inverter would draw more amps but not take as long to heat the water, but still use more AH than the MSW depending on your version of hot enough)--voltage drop 0.8 volt.

Note the kettle also needs more water than needed for a cup to reach its minimum fill level marker, and it gets the water too hot. Yes I can use the propane stove with a pot of water and do it that way--if desperate!

However that is in the TC with the small MW and MSW. In the MH the MW is bigger and the inverter is PSW, so the kettle is a valid choice.

So that was pretty good IMO. For those kinds of high draws I would need four 6s at 50% SOC or 90/230 = 39% draw to stay above inverter alarm at 11 volts

48 Replies

  • Seems to hold voltage about the same as my old set of four GC2.

    Has charging performance been measured? Such as how fast does the SiO2 get charged and when does it start to taper the current?
    What is the temperature compensation below freezing?
  • 3_tons's avatar
    3_tons
    Explorer III
    I do view these findings very interesting and ‘demonstrable objective’ :), Many Thanks for posting this!! No doubt, a solid case can be made for SiO2’s, particularly regarding cycle life (per Azimuth), uber high discharge amps, no sulfating (no equalizations needed), and the ‘hands down’ cold weather king…At first glance, initial acquisition cost might put some folks off (as with a few LFP…) but in many ways superior to some other types, thus, (similar to LFP’s…) for some folks, likely can be well justified over the loooong haul…

    Again, Great Post !!

    3 tons
  • otrfun wrote:
    BFL13, interesting info, thanks!

    How low (of a SOC) can a SiO2's be safely discharged on a regular basis?

    Your max load appears to be ~90a. Maybe I missed it, but will the voltage on your 200ah bank of SiO2's stay above the inverter's low-voltage cut-off while under a 90a (.45c) load at its minimum recommended SOC?


    They say you can run them down to Zero SOC many times no problem, but I have seen ads for AGMs saying the same thing.

    So you can run them down past what would trip the inverter to just run ordinary low amp RV loads ok

    The voltage drop is also from wiring not just from the batteries, so if I had fatter wiring and all that, the inverter could go lower in battery SOC before tripping, so my result could be different from another guy's with the same battery

    I count the "0.45C" as using the C at the time, not the rated C when at 100% SOC, so watch for that when reading my numbers. Eg the 90 amps when the 200AH bank is at 110AH is 90/110 = 82% draw the way I do it.

    I only took it to the inverter alarm at 11v not to the cut off at 10.5v so I don't know how much farther down in SOC it would go to get to 10.5

    They have a somewhat higher voltage per SOC than Flooded batts so that helps with going lower in SOC before tripping the inverter too.
  • BFL13, interesting info, thanks!

    How low (of a SOC) can SiO2's be safely discharged on a regular basis?

    Your max load appears to be ~90a. Maybe I missed it, but will the voltage on your 200ah bank of SiO2's stay above the inverter's low-voltage cut-off while under a 90a (.45c) load at its minimum recommended SOC?
  • wa8yxm wrote:
    Just so you know... I always assumed PSW inverters were not as efficient as MSW at turning 12 into 120.

    Finally I researched... Peak efficacy is 89-90% on one 90% on the other. Identical.


    Still has the PSW draw more amps than the MSW same load. So it is about the time being shorter for the PSW to beat the MSW for AH

    150 amps for 3 minutes (0.05 H) = 7.5 AH
    125 amps for 4 minutes (0.067 H) = 8.4 AH

    But if it is a spud for as long as it takes to get soft enough by poking it with a knife, IMO you can't tell the difference for it being ready to eat if you make it 7 minutes for each case--in which the MSW then wins for having fewer AH.

    150A x 0.12H = 18 AH
    125A x 0.12H = 15 AH
  • wa8yxm's avatar
    wa8yxm
    Explorer III
    Just so you know... I always assumed PSW inverters were not as efficient as MSW at turning 12 into 120.

    Finally I researched... Peak efficacy is 89-90% on one 90% on the other. Identical.
  • Another interesting, educational report. TY.

    Price seems high even in Canadian dollars.