pianotuna
Jun 08, 2013Nomad III
Hi,
Heat was one reason why I wired for series/parallel @ 33 volts into the MPPT controller. The other (main reason) was a #10 prewire. Finally the panels are nominally 16.5 volts--a little low for good MPPT response. The reason for MPPT at the time was the $5.50 cost per watt for panels.
Salvo wrote:
5% or 8%; all about the same. Temperature and battery voltage have a huge effect on mppt gain. I just looked at some measurements I took a few years ago when I held battery voltage constant at 12.25V. This is where mppt is at its best. It doesn't get better than this. At 9am gain is about 20%. With panel warming up gains drop from here, down to 11% at noon. In the afternoon gains are about 8%. At 9am panel temp is 30C, and at 1:30pm temp is about 50C while ambient is 21C. The 29C temperature rise just killed mppt gains. If I were to let battery voltage rise, gains would be much lower.
20% of battery charging time could be in boost mode, while 80% is in absorption. That means you're only using the mppt feature for only 20% of the daily charging cycle. If you're in boost for 3 hours with mppt, then you're only 3.15 hours @ 5% gain or 3.3 hours @ 10% gain when using pwm. The rest of the time both systems charge at the same rate. MPPT is getting plenty of hype.
Salpianotuna wrote:
Hi Salvo,
I thought you said 8%?
Having RV issues? Connect with others who have been in your shoes.24,410 PostsLatest Activity: Sep 01, 2026