All the "load" settings can be ignored, since you should only have four wires into the controller, with the two load wire terminals empty.
Your charge voltage of 14.8 is good and with temp comp will see 15.2 at 35F, so be over 15v. Many inverters shut off if they see voltage that high at 15, so it is good to co-ordinate the inverter's high limit with the solar's.
Two hours of 14.8 may or may not be enough before dropping to Float. That one you can play with to suit each situation.