Chris_Bryant
Mar 30, 2017Explorer II
On the SF series, I have found the most common failure is the limit switch- if you open the inside panel (not outside), it is right there. Often simply unplugging and replugging the leads will fix it, due to oxidation on the terminals. Next is sail switch.
Sequence of operation-
- Thermostat calls for heat
- relay (or board) starts blower
- sail switch closes at ~75% speed
- board gets power- ~30 second purge cycle
- board fires spark and opens gas valve for ~7 seconds
- etc