saddlmup's avatar
saddlmup
Suburban SW6D
I replaced exact same unit, same wiring, plumbing, gas, followed instructions carefully, although they left a lot to be desired.
Water filled, propane ok. Absolutely nothing happens when I try to light it with the wall switch.
Is there a way to tell if the igniter is even alive? Tried jumping the 2 wires at the wall switch, with no results.
What can I check next?
  • 12V DC (+) comes form DC Dist Panel (fuse)
    Goes to ON/OFF switch
    Then to DC Junction Box on side of WH tank
    Inside box are 4 OEM wires
    RED...DC + to t-stats
    Blue...DC + from circuit board to fault light in switch
    Yellow & Green DC -/grd
    RED wire goes to high t-stat lug thru it then via hard wire to normal t-stat thru it and from lug to circuit board.
    DC Voltage from circuit broad to gas solenoids while sending high voltage to spark electrode
    Easiest place to check for DC Voltage is at t-stats
    Remove rubber cover (above gas valve with 'reset' buttons
    Check for DC voltage at RED wire on top lug----that comes from ON/OFF switch
    IF No DC then issue is inside junction box, at switch or with fuse
    Got DC ...then check for it at bottom lug.
    No DC..then top t-stat is tripped---push reset, wire is burnt into---replace set of t-stats (12V DC ones)
    Got DC...then check for it at gas solenoids WHEN you turn it ON (DC Power is only on gas solenoids for approx. 6 seconds while spark electrode gets voltage)
    Check that spark electrode is properly gaped (1/8"), high tension wire is tight/clean connection.
    Example of t-stats
    Left set is for 120V AC element
    Right set is for 12V DC propane
    Top is Hi temp/bottom is normal temp t-stats
  • Is voltage present at the switch, control board, thermostat?