Most likely cause is there is no ground wire connection...:W
Probably the receptacle is wired incorrectly and/or incomplete. Pretty easy to do if you're not an electrician. You don't say whether your receptacle is 30 or 50 AMP service. 50AMP has two hots, a neutral and a ground.
To easily check, use a meter and probe one of the hots and connect the other to the ground. You should show 120V on each leg. If not your ground wire is missing/broken/cut or was never installed.
To better help us help you, provide the NEMA number on the receptacle.....Dennis
HERE is more info...D
Probably the receptacle is wired incorrectly and/or incomplete. Pretty easy to do if you're not an electrician. You don't say whether your receptacle is 30 or 50 AMP service. 50AMP has two hots, a neutral and a ground.
To easily check, use a meter and probe one of the hots and connect the other to the ground. You should show 120V on each leg. If not your ground wire is missing/broken/cut or was never installed.
To better help us help you, provide the NEMA number on the receptacle.....Dennis
HERE is more info...D