mena661 wrote:
Fuses are to protect wiring, correct? If that is really so then I have a question posed as an example. Suppose I have a 55 amp converter. It is connected to a bank of batteries with 4 ft of #4 wire. ~180 amps is the max rating for 105C #4 wiring. What would be the point of fusing this wire if a catastrophic failure of the unit only sends a max of 55 amps down the wire?
The converter side is rarely fused, because the converter is inherently current limited.
The battery side is always fused though.