The correct receptacle is the four pin NEMA 14-50R.
Problem is what is the house wired with. Older homes were wired with 6/3 with NO ground. The ground in the range was jumpered to the neutral.
Newer homes are wired with 6/3 with ground. The neutral and ground have the own wire to the service panel.
I would verify your wiring first, then get the correct range pigtail.