That model is rated for 3.5 KW continuous, and has an automatic voltage regulator circuit - so it should be capable of powering just about any microwave oven.
Microwaves aren't particularly picky about the AC line frequency, so it should still work even if the frequency is a few Hz off.
You might try measuring the AC voltage at the same receptacle the microwave is plugged in to - while the microwave is running. Look for excessive voltage drop as soon as the microwave is turned on.
Microwaves aren't particularly picky about the AC line frequency, so it should still work even if the frequency is a few Hz off.
You might try measuring the AC voltage at the same receptacle the microwave is plugged in to - while the microwave is running. Look for excessive voltage drop as soon as the microwave is turned on.