enblethen wrote:3500/240=14.6A. 14.6A on each hot leg is inadequate for the typical MW. Switch to the other plug as suggested.
I better clarify that the twist lock is 120/240 four wire. 14.6 amps total, indicating it would be somewhere around 7 amps per 120 leg.