What error code is showing? Does it run small loads fine?
nature power 2000w manual
Understanding the Error Code
Code Condition Corrective Action
E01 Unit has sensed input under voltage
and has shutdown
Recharge battery immediately and
restart unit
E02 Unit has sensed input over voltage
and has shutdown
Check battery voltage or if any external
charger is connected to the battery bank
E03 Unit output has sensed overload or
short circuit and was shutdown
Check load connected to the output.
Reduce load and restart the unit
E04 Unit has sensed internal
temperature was high and has
shutdown
Turn unit off and wait for 15 minutes
before restarting. Check if any object
has blocked the air flow of the unit
E05 Unit has sensed input voltage is low
and warning occurs
Recharge battery as unit will shutdown
shortly
E06 Unit has sensed load connected is
close to overload shutdown limit
(Not applicable for 38210, 38215)
Reduce load
E07 Unit has sensed internal
temperature is high and is close to
thermal shutdown limit
Reduce load and check if any ventilation
of the unit is blocked
nature power 2000w manual
Understanding the Error Code
Code Condition Corrective Action
E01 Unit has sensed input under voltage
and has shutdown
Recharge battery immediately and
restart unit
E02 Unit has sensed input over voltage
and has shutdown
Check battery voltage or if any external
charger is connected to the battery bank
E03 Unit output has sensed overload or
short circuit and was shutdown
Check load connected to the output.
Reduce load and restart the unit
E04 Unit has sensed internal
temperature was high and has
shutdown
Turn unit off and wait for 15 minutes
before restarting. Check if any object
has blocked the air flow of the unit
E05 Unit has sensed input voltage is low
and warning occurs
Recharge battery as unit will shutdown
shortly
E06 Unit has sensed load connected is
close to overload shutdown limit
(Not applicable for 38210, 38215)
Reduce load
E07 Unit has sensed internal
temperature is high and is close to
thermal shutdown limit
Reduce load and check if any ventilation
of the unit is blocked