You don't have "165A available". 165 AH bank of 2* group 24 means 82 AH available (they are AH, btw, not A).
With this bank I would avoid running any MW. It will run, but the batts won't like 40A current per battery, their life will shorten. Besides, guys were right that you won't be able to cook anything - you'd use half the bank in less than 60 minutes then. For warming the meals and making coffee you don't really need MW.
With this bank I would avoid running any MW. It will run, but the batts won't like 40A current per battery, their life will shorten. Besides, guys were right that you won't be able to cook anything - you'd use half the bank in less than 60 minutes then. For warming the meals and making coffee you don't really need MW.