- GdetrailerExplorer III
Harvey51 wrote:
Would it be fair to suggest that the safety ground system is a waste of copper when all circuits are GFCI protected? If the cost of copper and electrician labour keeps rising it may become cheaper to go with GFCI breakers instead of ground wiring.
No.
Think of it as a "belt AND suspenders" type of thing.
Some electric items simply cannot be "double insulated" and therefore a "safety ground" is an essential must have.
Some examples of items which can not be "double insulated" are large appliances like fridge, microwaves, stoves, washers, dishwashers and so on.. Some appliances which have critical role like a fridge are not required to be on a GFCI even if in a basement or garage (don't want a fridge to shut off from a false trip).
Safety ground also stops the "skin effect" some items can exhibit which due to natural capacitance often will allow a device to have some slight potential above ground.
This typically can happen to RVs using 30A 120V service with a extension cord that is missing the ground or has a broken ground wire.. Often called a floating ground on the RV chassis which will show 5, 10 or more volts and "bite" you when you attempt to touch anything metal on the RV while standing on the ground in bare feet..
GFCIs are just an extension of safety features, they are actually reliable and the technology has matured greatly..
GFCIs since they really do not "need" a ground to operate can be EASILY retrofitted into old two wire electrical systems to make those a bit more safe..
I have them in my kitchen, basement, outside and garage for 25 yrs now and zero false trips and non have failed..
I did have one fail in my TT but that was because it was a GFCI with outside exposure under a "in use" cover.. Unit got damp after some heavy rains and died.. - mikestockExplorer
Harvard wrote:
The under lying issue with "unexpected" GFCI tripping from an RV sub system is called "stray capacitance" which allows for stray current leakage. Every foot of wire has some stray capacitance and some loads have RFI capacitors across their AC input circuits. All this "Normal Capacitance" soon adds up to be a 5 mA current leakage.
Is there a solution? I actually tried using a portable battery charger to maintain house batteries but it has "smart" features that somehow won't reliably keep my house batteries charged. I attached at the point they feed the inverter with 12v. It gave me an error. - Harvey51ExplorerWould it be fair to suggest that the safety ground system is a waste of copper when all circuits are GFCI protected? If the cost of copper and electrician labour keeps rising it may become cheaper to go with GFCI breakers instead of ground wiring.
- DrewEExplorer II
That is assuming you don't have a neutral/ground fault somewhere in the RV wiring, or a bad water heater element, or a bad fridge element, or water intrusion in some electrical box, or some other problem.
It takes hundreds of feet of Romex to get sufficient capacitive coupling in the cable to be problematic, somewhere around a few thousand feet I think. The current requirements for electronic devices are no more than 0.5 mA leakage in RFI filters, etc. A properly constructed RV, one with no ground faults, generally should not cause a good quality, properly functioning GFCI to trip. I suspect, albeit without proof, that more than a few RVers have actual electrical problems or faulty appliances that go uncorrected because they chalk things up to "RVs and GFCIs don't work well together" rather than looking to see if there really is a problem to be fixed.
(I'm also a little surprised the NEC doesn't require GFCI protection for outdoor RV receptacles as they do for standard outdoor receptacles.) - Dutch_12078Explorer III
Harvard wrote:
mikestock wrote:
All this brings up another related topic. I know I'm wavering.
My RV is in a storage lot where a, low potential, outlet is supplied for each camper. An AC unit or electric water heater will immediately trip the main.
We, pretty much, only plug up to keep batteries charged. Nobody loads anything of consequence on the inverter or 12 volt system.
Every motorhome owner I talk with seems to have a persistent problem with the GFCI's tripping. The only thing we all have in common is that we all have an inverter. Mine is a 1500 watt Xantrex PSW.
Is there something inherent with motorhomes that could cause this? I know the 15 amp connections an campgrounds are GFCI, but I doubt they are used by motorhomes.
Can you imagine having your whole house protected by one 5 mA GFCI.
Why do we think a single 5mA GFCI is going to cope with an entire RV sub system. Just saying.
5mA is the leakage trip point, not the load trip point. As long as GFCI circuitry is built heavy enough to carry the intended load, it will work. For example, a 50 amp 2-pole GFCI breaker would handle a 50 amp RV at normal loading, yet still trip with a 5mA+ leakage. - HarvardExplorerThe under lying issue with "unexpected" GFCI tripping from an RV sub system is called "stray capacitance" which allows for stray current leakage. Every foot of wire has some stray capacitance and some loads have RFI capacitors across their AC input circuits. All this "Normal Capacitance" soon adds up to be a 5 mA current leakage.
mikestock wrote:
You can isolate the circuits and discover the offending issue. Or consider using a portable battery charger instead of the converter with entire RV system connected. A 5 amp rated charger should be plenty.
Is there something inherent with motorhomes that could cause this? I know the 15 amp connections an campgrounds are GFCI, but I doubt they are used by motorhomes.- Sam_SpadeExplorer
Because it WILL.
It is common practice to use a single GFI in buildings to feed/protect multiple outlets, even in different rooms, sometimes on different sides of the house.
I absolutely HATE having it wired that way.
It is a royal pain to have to search out the tripped GFI when it is in the other end of the house......or in the garage. - HarvardExplorer
Why do we think a single 5mA GFCI is going to cope with an entire RV sub system. Just saying. - DrewEExplorer II
ktmrfs wrote:
wa8yxm wrote:
Will it work: Perfectly
Does the GFCI care. On some of 'em the safety ground is not even connected.
the ground lug better be connected on a GFCI outlet or it is a code violation. And GFCI outlets sold today detect ground/neutral bonding so they must have a connection to the downstream ground.
If you have a safety ground conductor available, indeed it must be connected properly, both per the electric code and per common sense.
If you have an old electric system which lacks a safety ground, it is permissible by code to install a GFCI and so be able to plug in three prong cords (for grounded devices) without rewiring everything. Such an outlet must be labeled as not having an actual safety ground. Absent the GFCI, only ungrounded (two prong) outlets would be permitted to be installed.
Current GFCIs do detect ground/neutral shorts upstream and trip if they are found. I don't believe any of them require that ground and neutral be bonded downstream, but perhaps I am misinformed on that. It's not a universal requirement at any rate.
Having RV issues? Connect with others who have been in your shoes.24,344 PostsLatest Activity: Dec 26, 2025
