X3. Really sorry, but I agree that is a bad idea too. Good concept but poorly executed as it stands. It won't be CSA approved as an assembly nor will it meet NEC. But what do I know, just an EE....
3 x #10 and 1 x #12 wires in a red marrette is too many wires and won't meet code. Set screw connectors would have been better, especially with stranded conductors.
Anyway, why go to all that trouble when you can plug the separate 20 amp power inlet into the 20A recept. on a pedestal? As well, often there are only 30 amp recepts. on pedestals.
Oh, and that is the most humongously huge image I have ever seen on the internet, lol!
CA Traveler wrote:
TNGW1500SE wrote:
Sorry about raining on your parade but it isn't safe the way you have it. Just do the same thing using a sub-panel with proper breakers.
X2