Apr 17, 2021

50amp EMS w/surge

Will The EMS-PT50X 50amp EMS operate properly if plugged into 30amps? Need to know before I commit...No response from Progressive Ind.
  • I am going to take a stab that it won't allow power if you are only supplying power to only one of the "legs"..

    Page 6 of the manual..

    HERE

    "Example:
    The EMS shuts down power for low voltage on Line-1 and then power is
    restored. "


    In a nutshell it is supposed to not allow voltage to pass if it is below 104V.. Guessing that would also mean that BOTH L1 and L2 must have voltage higher than 104V..

    Page 5 seems to indicate that both L1 and L2 need voltages higher than 104V..

    "NOTE:
    If the display indicates an error code other than
    E 0 or E 10, the EMS will not allow power to the RV. "


    Now if your 30A 120V adapter were to supply voltage to both L1 and L2 then it "might" work but if unit is looking for L2 to be 180 degrees out of phase (the way it should be) then I suspect the unit won't pass voltage on to the trailer..

    But, hey, you might get lucky and the EMS doesn't care if L1 and L2 are in phase..

    All you can do is try it with the EMS and if it doesn't work just remove it or bypass it?