If your 2000w inverter's low voltage shutdown spec is 11.0v or less AND you use inverter to battery cables that have less than a 2% voltage drop at your maximum anticipated load, this should significantly reduce your chance of having a problem powering your inverter with 2 GC2 batteries if they're discharged as low as 12.2v (50%).
We power our 2000w Xantrex PSW inverter with 2 GC2 batteries. FWIW, we can power a small 1,500w space heater on high (~140 amps) with 2 GC2 batteries already discharged to 12.2v. Inverter input voltage under this load is approx. 11.2 to 11.1v--just barely above the Xantrex's 11.0v low voltage shutdown voltage. Yes, the low voltage alarm activates, but the inverter does not shutdown. We use 4/0 cable for the 13 ft. battery to inverter cable run which limits our voltage drop at 140a to .15v (~1.4%).
I might add we can power our 1,100w microwave for up to 40 min. with our 2 GC2 batteries before they drop to 12.2v.
We power our 2000w Xantrex PSW inverter with 2 GC2 batteries. FWIW, we can power a small 1,500w space heater on high (~140 amps) with 2 GC2 batteries already discharged to 12.2v. Inverter input voltage under this load is approx. 11.2 to 11.1v--just barely above the Xantrex's 11.0v low voltage shutdown voltage. Yes, the low voltage alarm activates, but the inverter does not shutdown. We use 4/0 cable for the 13 ft. battery to inverter cable run which limits our voltage drop at 140a to .15v (~1.4%).
I might add we can power our 1,100w microwave for up to 40 min. with our 2 GC2 batteries before they drop to 12.2v.