MitchF150 wrote:
Are you using any kind of extension cord to plug in? If so, make sure it's a beefy cord and not just your everyday orange one that's 50' long!
If you do, you'll lose a lot of volts and it will get hot pretty quick.
If you are connecting directly from the 30a trailer cable to the adapter to the outlet, you should be fine as long as you don't run anything more than a few lights.. No water heater on electric, no fridge on electric, no microwave and no hair dryers for sure!!
Good luck!
Mitch
50' of 16 gauge wire @120V with 18A of current is only 7V of drop, add the 1V of drop from 25' of 10 gauge RV cord and you're still at 112V, plenty. You'd only have a problem if the source voltage was 115V in which case you'd be close to the minimum for most motors. Step up a few dollars to a 12 gauge extension cord and you're under 4V of total drop which should be plenty even at 115V source.