BurbMan wrote:
Yes the breakers only isolate the hot, but the GFCI won't trip with the hot disconnected. Some things in the camper you can't "unplug", items like the converter and HW heater are usually hardwired.
If you start with the breakers, you can isolate what circuit the problem is on, or if the GFCI still trips with the breakers off then the issue is with the cordset.
Not true. GFCI’s can absolutely trip with the hot disconnected. They can test for and trip by simply having a neutral to ground short without any current flowing. So while turning off breakers may reveal something, it may not.
If ANY place inside the camper has a neutral to ground short, the upstream house GFCI will trip, not just with a power cord short.
To completely isolate, you may actually have to open the camper panel and disconnect the neutral wires until the fault clears.