The OP had a poor connection at the receptacle the cord was plugged into, plain and simple.
A poor connection causes resistance, and resistance causes heat and heat can lead to a meltdown. If the cord was new, the receptacle is def. the culprit. They get a lot of use & abuse. Plugging in live all the time causes pitting on the contact surfaces inside but you can't see inside them. Always check your plug blades periodically and ensure they're clean 'n shiny and use some emery cloth or sandpaper on them.
We were at a CG on the weekend and the receptacle was so loose the plug wouldn't stay in. The breaker wouldn't even work and turn on. They sent over their all-purpose handyman kid (in his 20s) and he put a new front on the pedestal box. Upon close inspection I noticed it was a used one that was in usable condition. The plug didn't fall out and breaker worked but when I went to unplug when breaking camp, I found the plug was rather hot. It never does that and the blades are in excellent condition so the replacement recept. was already in poor shape. Unfortunately, the NEC or local AHJ can't prevent a used replacement recept. or breaker from being installed.
We have a 30 to 30 amp 18" pigtail adapter for use when pedestal recepts. are in bad shape. That way, if it does overheat and melt only the adapter will get damaged.
valhalla360 wrote:
Funny thing is a 30 amp plug is only rated for 24 amp continuous load.
The breaker is also limited but it's variable exactly when it will pop if you are hovering right around the limit.
Nooooo... Sorry, but complete BS.
The plug on a 30 or 50 amp shore power cord (and the cord) is designed and UL listed to carry it's full rating indefinitely. Any molded case circuit breaker (like in a pedestal or panel at home) is also designed and UL listed to carry it's full rating indefinitely. A circuit breaker can even carry more than it's rating and the duration it can depends on for how long. Any electrical engineer can tell you this, it's electrical 101.
This website has a standard time-current graph for breakers and explains tripping time for overloads and short circuits.
If a breaker cannot sustain it's rating, then it's simply time to replace it. Breakers in pedestals are often in climates where they are subjected to large swings in humidity and temp. season to season, plus they get a lot of wear from switching on and off all the time. However, it's not often anyone is going to be drawing near 30 amps for sustained periods of time. I installed an LED ammeter inside (along with voltmeter) and the current rarely gets much above about 20 amps.
Note that extension cords and adapters are not required to be UL listed and if buying new ones, avoid any that aren't UL listed as they could be made poorly made and lead to overheating.
If you have a detachable power cord, also ensure the blades at the twist lock power inlet are also kept clean 'n shiny. If it's an older shore power cord and it gets hot at the twist lock connector end (the female end), it may be time to replace the cord or connector.
Below are a couple of examples of damage from overheated shore power cords. Don't let this happen to you.