Gdetrailer
Nov 17, 2014Explorer III
Nvr2Loud writes “You are not correct. A 50 amp 240 volt shore power breaker is capable of producing 50 amp maximum (not 50 amp per line)
If it was DC current, you would be correct, however it is AC current we are discussing.
An entire house with dual 100 amp main breakers is capable of running 10 amps total, not 200 amp.”
:R :h :E ??
Sorry but you are wrong.
240V requires a double pole breaker, this breaker is designed with a common trip for BOTH “poles”, the poles are Line1 and Line 2. EACH “POLE” of the breaker is rated for 50A.
Keep in mind 240V x 50A is 12,000W.
120V x50A is 6,000W
Each pole (line) on a double breaker is to protect the 120V LINE on that pole.
The 240V from the utility comes from a transformer, L1 and L2 come from the ENDS of the transformer windings.
To get 120V you NEED to provide some sort of split in the voltage, this is done at the transformer via what is known as a CENTER TAP.
The CENTER TAP IS USED AS THE NEUTRAL WIRE.
So if you looked at the waveform from the neutral you would see that the L2 peaks are the OPPOSITE of L1.
Think of it like you have two 6V batteries in series and the center tap of the transformer is the connection in between the two batteries.. Only in this case we are dealing with alternating current.
I would suggest you study the diagram below..
In the AC world the two 120V lines are in series to provide 240V and the center tap allows us to get TWO 120V lines.
Typically in a RV there are no 240V “appliances” and what you get is TWO 120V AT 50A lines (although you could potentially add a 240V device).
The last time I checked, TWO 120V lines at 50A IS 12,000W..
Not sure where you were going with the last part but it is not correct either..
A home service load center which is 100A is not “dual breakers”, they are TWO POLE breakers with a common trip and EACH pole handles 100A at 120V. EACH pole handles 12,000W and for 240V you get 24,000W for that panel.
I would highly recommend you take a real good look at the following link which will explain why you are wrong.. (it is where I found the diagram above but the link has text for you to follow along with)
HERE
In the mean time I would recommend that you should not start poking you fingers inside any electrical box..
:R :h :E ??
120V x50A is 6,000W
HERE
44,067 PostsLatest Activity: Jun 02, 2026