Hey guys, could really use your help on this one.

I got a wildwood TT with a 15,000 btu a\c unit. I also own a yamaha 3000 watt generator with boost.

When I first got the genset, it could start the a\c. It struggled very hard, but it would start it. Now, it seams like it won't at all. I've tried everything; spooling up the geneset with a small load, turning all electric off ( lights, fridge, water heater,etc..) and still no go. Any ideas?

13 Replies

  • Don't forget to turn off the converter and may need to add a hard start kit to the A/C. :)
  • 15000 btu on a 3000 watt genny is going to be marginal. It's the start up that is difficult, once it's running, doesn't draw nearly as much.

    A couple suggestions. Google hard start capasitor mod and check and see if your ac has one. If not, add one.

    Secondly, use your circuit breakers to kill everything but the ac that has a circuit breaker for 110v. Give it a try then and then once it's running, you should be able to power back on.

    You don't say but altitude can make a genny not run at peak power so if you've been camping at higher altitude than when it ran before, that might be part of it. Also hotter weather makes the ac work harder. Mine will start up while plugged into the house in the spring but blow a circuit breaker in the summer because it needs more than the 20 amp circuit can provide it.