Gdetrailer wrote:
CA Traveler wrote:
CGs like houses are usually wired to supply about 40-50% of the pedestals amp rating. Hence every summer low voltage is common with lots of A/Cs running.
In my experienc 50A pedestals are not likely to have low voltage due to better wiring and 12000W rating vs 3600W for 30A.
????
No, not true that CGs like "houses" are wired to supply 40%-50% of the service rating.
If it was there would be many more service entrance wiring fires.
Actually, the NEC code allows for derating factor and that is common. And the panels main CB would trip to provide protection from overloading and fire.
Here are 2 examples:
My 2006 house built to code has a 200A panel or 48,000VA max and of course the main CB would trip if either leg exceeds 200A. Adding all of the single and dual CBs in the house panel yields 97,000VA or 51% derating..
In 2007 I was in a new CG that had a 100,000VA transformer supplying 18 50A sites. The sites totaled 216,000VA or 54% derating. Another view is that the sites are limited to an average of 23A@240V not 50A or 46A@120V not 100A.
My house has never tripped the main CB and I’m confident that the CG has never had 18 50A rigs averaging more than 46A@120V. Otherwise it would be extremely and wasteful and costly for everything from the utility to the transformer to supply 100% of the power.