Huntindog wrote:
Heavy duty registers are available. I replaced all of mine. The new ones won't break. IDRC where I got them, but a search will turn it up.
And X2 on the caution about restricting airflow. I personally would not cover or block off any of them. The heater installation, manuals state just what is needed. Maybe you can block it off, or maybe you can't. You simply do not know if YOUR TT has more airflow than is needed. Restricting it below what is specified will cause the heater to overheat the combustion chamber..... There SHOULD be a safety switch to shut it down in that case... But it may not work , and I believe on at least some heaters, it is a one time switch.... IOW, when it blows, it needs replacing. This is so people do not keep running a heater that continuously trips the safety switch... A heater that does that NEEDS to have a repair done.
If you are dead set on closing off that vent... See if you can add one where it will be useful.
I did that on my TT, it was an easy cheap project, and now the BH has the heat it needs.
It's called a 'high limit switch'....will shut down furnace if heat exchanger air temp rise too high (depending on model 130*F---190*F)
Self resetting when temp drops
Atwood Water Heater uses a one time 'thermal fuse' blows at 190*F and has to be replaced
Closing off register MAY limit airflow enough to cause furnace to shut down.....MAY
Try it...if furnace shuts down don't do it again