Gdetrailer
Aug 18, 2022Explorer III
spoon059 wrote:
Couple of thoughts... I suggested a mini-split which would draw significantly less than 21 amps or 1000 watts. From what I am reading a 12K mini-split pulls about 4 amps at maximum draw and throttles down substantially from there. I've seen plenty of Youtube videos of people running mini-splits off 8 panel solar systems with larger battery banks. Its doable, likely for about the cost of a typical onboard generator.
I simply don't want to pay those prices to make it silent, so I'm leaning back towards a $1200 Honda 2200 for the occasional dispersed camping.
But, it is absolutely possible with a reasonable solar array and not nearly as expensive as your model.
Doubtful.
Looked at a MR Cool 12K BTU mini split which uses inverter technology compressor, calls for minimum 14 ga wire which would be a "15A" circuit..
They are claiming 7.8-10 BTU/watt for efficiency in their brochure HERE
4A at 120V is 480W and at the max of 10 BTU per watt that gets you 4800 BTUs worth of cooling.
You would need to find a mini split well under 9K BTU that might get you closer to that magical "4A" at 120V range.
4A at 120V is most likely a very small window air like 5K BTU if it was using inverter technology compressor and low fan speed.. But unless you have a small TC or sub 17ft TT, 5K BTU isn't going to cut it in 90F+ temps with high humidity.
Lets face it, in most RVs even a 13.5K BTU A/C barely gets it done.
On edit..
Found a Bosch 5K mini split that runs on 120V HERE (out of stock of course).
So, there is some very small 5K BTU mini splits out there, but in most RVs 5K BTU isn't going to be of much help.
You almost need to check on sizing the system, found a guide on sizing a mini split (or any A/C for that matter)HERE
"To determine the size of a mini split, calculate the square footage of the room and multiply it by 25 to obtain the cooling capacity needed in BTU. Then, select the nearest mini split size based on the calculated BTU.
For instance, a 500 sqft room requires a 12000 BTU mini split because 500 sqft multiplied by 25 is 12500 BTU and the nearest mini split size is 12000 BTU.
As a rule of thumb, we use about 25 BTU per square foot to calculate the cooling capacity needed for a room. Because mini splits have several fixed capacities, we have to select the one that matches our needs.
But, we don't always need to use a rule of thumb of 25 BTU per square foot. Generally, anywhere between 20-30 BTU per square foot is acceptable to be used to calculate the capacity needed for room air conditioners such as a mini split.
However, the rule of thumb of 20-30 BTU per square foot is meant for insulated rooms or houses.
So, if your room or house is not insulated or, the insulation is known to be in poor condition, you need to double the rule of thumb figure or use 40-60 BTU per square foot to calculate the capacity needed thereby choosing the right mini split size."
RVs are very poorly insulated (R3 or less in walls and roof and R2 or less in the floor) and have single pane windows so landing on the oversized system typically is your better choice.
In my case, I have a 26ft TT, using 60 BTU per square ft gets me 12,480 BTU.. The 13.5K BTU roof air barely got the job done.. Now I have two Window units placed in cabinets.. 10K BTU for the main area and 6.5K BTU for our master bedroom.. Now we no longer lack for cooling.