Just a point .. When selecting an inverter you need to consider the startup load for the compressor, not the runtime load. If you size the inverter for the run load, it likely won't be able to start running the fridge. (Startup load on a compressor is quite a lot higher than the run load.) Most fridge's don't provide this information, but 4-5x is usually sufficient.