Twosees wrote:
Have shut them all off but still have the same problem. all of the receptacles work fine when plugged into my house receptacle but not into the inverter
yes
but arent you using the shore cord then
and with the inverter it won't work from the shore cord
or any other 'bypass', except the GFI circuit
but when using your 'work around' (you did not say no to the suicide cord) with the GFI the inverter doesn't alert
now why would that block it ?
all breakers off should isolate all circuits leaving only neutrals and grounds connected
you have a neutral to ground short in your new trailer
it can't be a hot short, or it would trip shore power breaker
i would start at the shore power junction box and work my way thru
to the breaker panel, then each circuit
there is an easy test
make a ground to neutral bond plug, and plug that into the inverter
nothing else and turn it on
see if it gives you the same alarm
if it does, thats proof of the problem in the TT