SoundGuy wrote:
And BTW, in the interest of accuracy it's spelled "semantics". :W
โApr-19-2019 03:26 PM
ktmrfs wrote:
yup, goes back to NEC code that says neutral and ground should only be bonded at the main panel, no where else downstream. So, since a trailer is meant to be plugged in downstream of the main panel, ground and neutral are NOT to be bonded in the trailer.
And most stand alone generators also don't bond ground and neutral for safety reasons.
So, yes an EMS will detect the"fault". And the solution is to either have a bonding plug in the generator or turn off the EMS.
โApr-19-2019 12:15 PM
SoundGuy wrote:
You really don't have an "open ground" as your EMS is telling you, it's really a floating neutral.
Bobbo wrote:
You can ignore the sematics lesson here. What you call it really doesn't matter.
SoundGuy wrote:
Bonding the genset's neutral to ground is the solution.
Bobbo wrote:
But, he still agrees that pianotuna's solution is the correct one.
โApr-19-2019 10:35 AM
โApr-19-2019 09:33 AM
โApr-19-2019 07:00 AM
pianotuna wrote:
Hi,
Generators have a floating neutral.
You can correct it by adding a "bonding plug" on the generator.
The easiest way to do a N-G Bond is to create a N-G Bonded Edison Plug, this is done by simply buying a replacement male plug and wiring the Neutral (White Wire/Silver Screw) to the Ground (Green Wire/Green Screw) using a 12-14 Gauge piece of wire. Just make darn sure you donโt wire the Hot leg tot he ground. Then when you need to power something like a RV or HE Furnace with your generator you plug it into a empty outlet.
SoundGuy wrote:
You really don't have an "open ground" as your EMS is telling you, it's really a floating neutral.
SoundGuy wrote:
Bonding the genset's neutral to ground is the solution.
โApr-19-2019 06:43 AM
sgfrye wrote:
... bonding plug mentioned should work but honestly ive used the generator many times with no ems and never had a problem.
โApr-19-2019 06:41 AM
pianotuna wrote:
Generators have a floating neutral.
pianotuna wrote:
You can correct it by adding a "bonding plug" on the generator.
โApr-19-2019 06:09 AM