CA Traveler wrote:
The rig is designed to use more power. Multiple A/Cs, HW, MW, etc and you may want to push that additional button but can't - The 30A pedestal CB will trip.
I added an additional circuit with 2 plugs mostly for ceramic heaters. For 50A pedestal it plugs into an existing basement outlet. For 30A I run an extension cord to the pedestal (most have 30A and 20A outlets). Others have modified a AC power wires so it can be run off of the extension cord. By all means use a heavy extension cord and not the typical home cord.
If you are not aware 50A is 240/120V 4 wire. In RV speak this simply means you have two 50A 120V circuits for the rig or as some like to say 100A available vs the 30A pedestal.
Jun-04-2018 01:52 PM
Jun-04-2018 11:30 AM
Fisher Bill wrote:With a 20/50 adapter(s) you should have power on both 50A hot legs. You have some other problem.
This explains why I have a dead set of outlets while shored up at home with a wimpy 15A to keep things running while we're remodeling the kitchen, missing that second leg from the service...
And I wouldn't even think of using the AC but we can get a bag of popcorn out of the microwave at least.
Jun-04-2018 11:19 AM
Jun-04-2018 08:58 AM
nayther wrote:Yes
so if I am plugged into a 30 amp, using a dogbone adapter to connect my 50 amp RV can I still use a 50 amp surge/power protector even though only one leg of the 120 is hot?
Jun-04-2018 08:34 AM
May-22-2018 04:44 PM
May-22-2018 11:12 AM
May-22-2018 09:49 AM
May-22-2018 09:35 AM
May-22-2018 09:27 AM
centerline wrote:Sorry but just about everything you posted in incorrect.Me Again wrote:
You still should install a 50 surge protector.
While on a 50 amp outlet, if you loose neutral you burn up all your AC items with 240V across them.
I agree strongly with using a surge protector (with combined auto transfer switch if you have a hardwired generator onboard)....
BUT.. as for burning up all the ac appliances if the neutral leg should be lost for some reason, I dont see how this is even possible unless its wired incorrectly INSIDE the RV...
the 50a shore power has the potential of supplying 240volt power to the unit, but the power panel INSIDE the rv is where the 120v would have to be combined to create the 240v power. this is not the case on most RV's... but the high end units with a washer/dryer option or household range will have the 220v option inside (or anyone who knows what to do could wire a circuit in)
bottom line is, on a 50a circuit, there are 2 separate legs of 120v power that are "out-of-phase" with one another coming in to the rv (if the 2 legs of 120v power were "in-phase" with one another, like on a generator, there would no option for 240v power), and these are NOT combined in any manner except at the 240v appliance itself... and in the USA the neutral is only acting like a ground in 240v circuit, and without it the appliance still works like normal. but ALL the 120v circuits will be lacking power (because half of its circuit has been lost).. but the appliances will be fine.
some countries of the world use only 2 wires to supply their 240v power, and not the three that we use here in the US..
but yes, one CAN absolutely fry all their 120 volt components if they dont know electricity, and yet try to do their own wiring inside the RV distribution panel or on the shore power side of it...
May-22-2018 08:43 AM
Me Again wrote:
You still should install a 50 surge protector.
While on a 50 amp outlet, if you loose neutral you burn up all your AC items with 240V across them.
May-22-2018 06:49 AM
May-22-2018 06:01 AM