Two ducted duo-therm A/C units on one thermostat control box. Both units would periodically stop running for 1-3 hours (intermittently trying to come on for a few seconds) and then come back on. Temperature in the bus usually didn't match what was on the monitor (too hot or too cold). Shop replaced the #1 unit control board (this one eveidently has an impact on functioning of #2 unit). Minimal difference. Next disconnected the remote sensor on #1 unit. All appears to be working properly now.

My question is do I need to replace the remote sensor? If it's not needed, why is it there in the first place? What am I missing here?
2003 HR Imperial 40 PKDD
4 REPLIES 4

Executive45
Explorer III
Explorer III
Solution is posted HERE
We can do more than we think we can, but most do less than we think we do
Dennis and Debi Fourteen Years Full Timing
Monaco Executive M-45PBQ Quad Slide
525HP Cummins ISM 6 Spd Allison
2014 Chevrolet Equinox LTZ W/ ReadyBrute
CLICK HERE TO VIEW OUR TRAVEL BLOG

bgholson
Explorer
Explorer
Yep, I have the heat pumps with comfort control box. Thanks for the link
2003 HR Imperial 40 PKDD

MountainAir05
Explorer II
Explorer II
http://bryantrv.com/docs2/docs/acservice.pdf

PAGE 34 C11

tell you how to check them out. You did not state which model you have so this is might be a general manual. comes in handy when you have a issue. Save for further use. Post back

dougrainer
Nomad
Nomad
1. I assume you still have the 2003 HR?
2. If so, there are 2 ways to sense temp on your 5 button Dometic CCC system----1. The Main tstat IS the sensor for Zone 1 and you have the remote sensor in the bedroom area for Zone 2---2. They elect to NOT use the tstat as the Zone 1 sensor and use a standard Temp Thermister like the one in the bedroom. They usually do this when they mount the wall tstat in an area that is not good for sensing the interior Zone 1 temp
3. IF you disconnect the Zone 1 wall Temp thermister, that makes the WALL tstat the temp sensor whereever it is located.
4. The Zone 2 is indeed run thru the Zone 1 control board in that the communication goes thru the Zone 1 board, but the Zone 1 board does not control any aspect of the Zone 2 AC unit.
5. Do you have the low profile Penguin series model AC units? If so, the odds are from the age of the RV that the communication phone type canles at the AC units are corroded from humidity during the past 10 years. Very common on older Penguin model AC units. You need to check and verify all of the phone wire type connections at the AC units. Doug