AC shuts off after only running a few minutes

I have a 2009 Monaco Camelot DSQ. It is the 42' model with 3 AC's on the roof. When I turn them on they only run a few minutes and then shut off. The thermostat goes blank. After 5 minutes or so they kick back on, the thermostat's screen comes back and all is normal. Then they shut off, etc.

What I know - it happens with both 50amp service and gen power.
Nothing else in the coach seems to be affected.
The EMS recognizes 50amp or gen power and shows uninterrupted power to the AC(and everything else) even when the AC units shut down.
All three units shut down and fire back up at the same time
We replaced the thermostat and the problem remained exactly the same.

EDIT FOR MORE INFO -
Rear AC and middle AC run perfectly when they are running solo or together.
Front AC cuts out running solo and/or kills everything when running with the other units.

So...the problem is the front AC unit.

Where do I look next?