holstein13 wrote:
I like the idea of the separate 30 amp plug for when you are parked. You are far less likely to trip the breaker that way. I did a similar install with my old gasser and it worked out great. I agree that you don't need 30 amps however. 20 amps would work fine.
That's fine, but did you in fact run #10awg (30amp) wire or maybe something smaller like #12awg (20amp) or #14 (15amp) wire.
If not the #10 and considering the enclosed run to the A/C unit, I would most certainly be using a breaker of the proper value and you shouldn't be having any tripping problems, anyway.