rk911 wrote:
backhoemike wrote:
I run the Genny while traveling this trip about 1000 miles if I drifted over the line and hit the rumble strip my electric would blink off shut down everything about 45 seconds when I was back smooth road everything ran fine. I figure its a ground but don't know where to start, I have a 1995 newmar London aire any ideas or thoughts on whats going on?
i would first look at the genny side of the transfer switch
This strikes me as good advice. It would seem to me to be an intermittent (loose) connection or fault somewhere between the generator and the transfer switch, or perhaps within the transfer switch, since there's a time delay for it to come back on. A transfer switch generally has a delay before it switches over to generator power after it sees power (so that the generator has a chance to get up to speed and have the voltage stabilized).
I would suspect it's not the ground for the generator, as losing that would also make the generator lose 12V power and I assume shut itself down (when the control board loses power). I think typically RV generators need 12V power continually to operate. I may be mistaken.
At any rate, checking the wiring and connections between the generator and the transfer switch would be a reasonable way to start troubleshooting.