magnum ME 2012
terryflt
Hi
Can any of you good people tell me the difference between the
ME 2012 and the ME 2012-20B.
My unit is fried and I want to replace it but do not want to buy the wrong one.
Thanks
Terry
22 REPLIES 22
2oldman
GordonThree wrote:
The shore power cable..snip..is protected by the breaker inside shore power subpanel (panel), where the plug is. That breaker is only to protect the shore power cable, not any of the circuits inside the RV.
Ok, that makes sense.
But I'm not sure I understand "where the plug is." It sounds like you have a separate 'subpanel' for that breaker -or you would have said 'the main panel,' where the 30a main breaker is.
Question: When inverting, one 'must' size a breaker to protect the wire coming from the inverter's 120v output? By my calcs, that would be a maximum of a 16a breaker. (2000w/125v), which isn't much of a wire. What about surge.. which can be double that, or 32a?
(No wonder I installed whole house. I just don't overload the inverter.)
GordonThree
2oldman wrote:
Then this implies that the circuits in your RV are unsafe to begin with, because a 30a shore hookup is very capable of delivering 2000w.
Maybe I'm a little slow today... this doesn't yet make sense.
The shore power cable doesn't go directly to the microwave / air conditioner, it goes through a subpanel full of circuit breakers first, inside your RV.
The shore power cable is designed to carry its maximum load of 30 (or 50) amps, and is protected by the breaker inside shore power subpanel, where the plug is. That breaker is only to protect the shore power cable, not any of the circuits inside the RV.
2013 KZ Sportsmen Classic 200, 20 ft TT
2020 RAM 1500, 5.7 4x4, 8 speed
pianotuna
Nomad III
Nomad III
Hi,
So, plug the shore power cord into the 2012 when you want power. No sub panel required.
Regards, Don
2oldman
Yep, that's what it says.
OnaQuest
Simply put, the 2012 is designed with a single output, designed to feed a subpanel. The subpanel should have a main breaker with branch circuit breakers.
The 2012 20B is designed with two 15/20 amp outputs that already have branch circuit breakers installed in the Inverter to directly feed outlets or appliances.
diveman52
That's what the circuit breakers are for in the panel.
As for a 2000 watt inverter overloading a 15 amp circuit.I seriously dought that 1.6 amp over will hurt. I have seen lots of overloaded circuit in my time in the trade. It's amazing what 14, 12 or 10 gauge wire will really handle. There's a pretty good margin of safety built into the amp rating of wire.
If you look at the NEC tables it actually says #14 is good for 20 amp but to never put it on anything larger than a 15 amp circuit breaker.
40+ Years in Electrical construction.
Retired IBEW Local 595
Every Days Saturday
2008 Newmar Dutch Star 4035
2oldman
jhilley
2oldman wrote:
GordonThree wrote:
With 2000 watt output, the inverter could overload a circuit wired with 14 gauge wire (15 amp max), without overloading itself, creating a fire danger.
I understand, but what does that have to do with a subpanel? Does that mean you're supposed to inspect your circuits, and if they're 14awg, put 15a breakers in the subpanel?
Yes that is correct, however there is a little more to it than that.
2003 Winnebago Adventurer 38G F53 Chassis Solar Power
1999 Winnebago Brave 35C F53 Chassis Solar power
Handicap Equipped with Lift & Hospital Bed
1999 Jeep Cherokee Sport
1991 Jeep Wrangler Renegade
2oldman
GordonThree
The breakers are to protect the wiring, not the inverter.
2oldman
GordonThree wrote:
Without those on board breakers, a subpanel would be required to provide the over-current protection.
What's wrong with the breakers in a main panel? Any decent inverter will cut out if it can't handle the load.
wolfe10
2oldman wrote:
In unyalli's post it says 'without requiring an inverter subpanel.' What's that about?
With the two circuit breakers built into that inverter, they serve as the "sub-panel". So hots and neutrals for those circuits would be connected to the inverter output.
Brett Wolfe
Ex: 2003 Alpine 38'FDDS
Ex: 1997 Safari 35'
Ex: 1993 Foretravel U240
GordonThree
Since there are two 15/20 amp circuit breakers on board the inverter, you can wire it directly to outlets, or an appliance. Without those on board breakers, a subpanel would be required to provide the over-current protection.
2oldman