hohenwald48 wrote:
I think the progressive low voltage drop out is set to 104 volts. If that's a cheapo 16 gauge extension cord. You will have about 13-15 percent voltage drop so you would need at least 120 volts coming in to the cord to keep the voltage at the distant end above the Progressive drop out voltage level.
I suspect your problem has no relationship to the transfer switch but power disconnect is occurring due to the Progressive detecting a low voltage condition. The Progressive contactor is the thunk you're hearing and not the transfer switch.
I think you probably need a shorter and/or fatter cord.
โDec-22-2017 01:17 PM
โDec-21-2017 09:51 AM
tropical36 wrote:farmingdad wrote:
When I ran a 100 ft drop cord out to motor home to keep ref working the transfer switch keeps clicking on an off
Check the voltage at the source with it off and then at the load side with it on. The difference is the voltage drop and probably insufficient to activate the transfer sw.
If the fridge is your only concern, then just power it up directly.
โDec-21-2017 07:21 AM
farmingdad wrote:
When I ran a 100 ft drop cord out to motor home to keep ref working the transfer switch keeps clicking on an off
โDec-20-2017 06:37 PM
farmingdad wrote:Fridge is only 3 amps and should run fine with minimal drop. Even keeping the battery charged should be only one extra amp once the batteries are topped up. Should not have an issue. I highly suspect something else is running.
Yes it does have the progressive low voltage on it , that is problay what it is thanks
โDec-20-2017 05:53 PM
โDec-19-2017 09:51 AM
โDec-19-2017 09:31 AM
RLS7201 wrote:farmingdad wrote:
When I ran a 100 ft drop cord out to motor home to keep ref working the tranfer switch keeps clicking on an off
The transfer switch is in the normally closed position to shore power. It makes no difference what the voltage is. The transfer switch should not be trying to switch unless it sees voltage from the generator.
Are you sure it was the transfer switch clicking?
Richard
โDec-19-2017 08:40 AM
OLYLEN wrote:
Think you have it backward, default is Gen, when you plugin the transfer switch makes the noise. And then the electrons flow.
LEN
โDec-18-2017 05:10 PM
โDec-18-2017 04:57 PM
โDec-18-2017 04:24 PM
โDec-18-2017 03:25 PM
โDec-18-2017 09:49 AM
farmingdad wrote:
When I ran a 100 ft drop cord out to motor home to keep ref working the tranfer switch keeps clicking on an off