Dry camping for first time with new trailer and could not take a hot shower? I smell the propane at the water heater and it tick tick tick ticks and nothing. I manually started water heater with a lighter, it lit but wont say on? The LP light switch stays on and after a few attempts the DSI FLT light comes on? Should I take it back to the dealer? Any troubleshooting tips?
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
โOct-21-2019 08:22 AM
It is a 99*C and can be purchased in packs of 5 for cheap or the pre-made pigtail for a bit more.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
โOct-17-2019 05:32 AM
jmatteis wrote:
Not sure if I have the same issue... new trailer, with atwood 6 Gallon LP water heater. when I turn on the heater inside, dsi light is on, goes off, and the heater tries to light. Does this 3 times before staying in a fault state. I have gone out and watched the heater when it does this. I have no spark, it opens up for a few seconds then turns off. If I light it manually with a BBQ lighter, it stays lit for that few seconds, but then goes out and the heater does that same cycle twice more. Have tried removing the inline Thermal cutoff, and plugged the lead in direct, still the same issue. Lines should be bled, as the stove, heater and fridge all work fine. Propane tanks were new when we got it, but purged before filled. It is under warranty, but thought if it was something I could fix on my own, I'd love to do so before towing it to a service center.
I have checked the 2 amp on board fuse, it's good, as far as I can tell all fuses in the inside panel are good as well. There are a couple of LED's on the board that I have never seen lit, so don't know if they are diagnostic or not.
Best to start a new thread, rather than asking here.
2018 Coachmen Catalina Legacy Edition 223RBS
1991 Palomino Filly PUP
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
โOct-16-2019 02:50 PM
If you "let go" of the light setting two quick, the gas shuts down.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
โOct-13-2019 12:53 PM
I have checked the 2 amp on board fuse, it's good, as far as I can tell all fuses in the inside panel are good as well. There are a couple of LED's on the board that I have never seen lit, so don't know if they are diagnostic or not.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
โOct-05-2019 07:55 AM
Bob/Olallawa wrote:
Clean the contacts at the board and try again. If that doesn't do it, it sounds like a new control board is in order. If warranty is still good take it to the dealer if not order a dinisor board replacment.
No. People make this mistake so frequently the Atwood manual even has a warning about NOT replacing the board. They hardly ever fail.
Some of the older Atwood water heaters had issues with loose connections to the board. I actually had to put a metal binder clip on the harness connector to keep it tight. Eventually I also had the ignitor burn out. That was a $10 replacement. The ignitor did spark but the flame detector portion stopped working.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
โOct-05-2019 06:09 AM
Jeff - 2023 FR Sunseeker 2400B MBS
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
โOct-05-2019 05:28 AM
Old-Biscuit wrote:
Good grief........
Your spark electrode is double duty.
Provides pathway for High Voltage Spark to ignite the gas
THen it proivides pathway for the 'rectified' current produced by the flame burning that is used as the flame priving signal ----just milliamps but enough for circuit board to sense that dc current
W/O circuit board receiving that signal it drops DC to gas valve so raw fuel desn't accunulate
You have gas flow (cause you CAN lite it with BBQ lighter)
You have Spark cause you can hear it CLick, CLick, Click
Circuit board is sending the DC to gas valve/spark electrode and is locking out the operation after 3x failed attempts (Fault Light comes on)
*Spark electrode gap ---too narrow/too wide ---no ignition (1/8" - 3/16")
*Spark Electrode wire connection...MUST be clean and tight. High Voltage can flow but the milliamp current can easily be stopped
*Spark Electrode MUST be engulfed in main flame when it ignites otherwise milliamp signal will not be sensed
*Spark Electrode must be clean...no soot.carbon----clean it using emery cloth
*Flame Spreader Plate (round disc) at end of burner tube must be squared/parallel with end of burner tube to properly spared flame out when it ignites
*Grounds.......MUST have good clean/tight grounds
*Connection at/on circuit board must be clean/tight
This is the correct answer
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
โOct-04-2019 08:28 PM
Your spark electrode is double duty.
Provides pathway for High Voltage Spark to ignite the gas
THen it proivides pathway for the 'rectified' current produced by the flame burning that is used as the flame priving signal ----just milliamps but enough for circuit board to sense that dc current
W/O circuit board receiving that signal it drops DC to gas valve so raw fuel desn't accunulate
You have gas flow (cause you CAN lite it with BBQ lighter)
You have Spark cause you can hear it CLick, CLick, Click
Circuit board is sending the DC to gas valve/spark electrode and is locking out the operation after 3x failed attempts (Fault Light comes on)
*Spark electrode gap ---too narrow/too wide ---no ignition (1/8" - 3/16")
*Spark Electrode wire connection...MUST be clean and tight. High Voltage can flow but the milliamp current can easily be stopped
*Spark Electrode MUST be engulfed in main flame when it ignites otherwise milliamp signal will not be sensed
*Spark Electrode must be clean...no soot.carbon----clean it using emery cloth
*Flame Spreader Plate (round disc) at end of burner tube must be squared/parallel with end of burner tube to properly spared flame out when it ignites
*Grounds.......MUST have good clean/tight grounds
*Connection at/on circuit board must be clean/tight
2007 DODGE 3500 QC SRW 5.9L CTD In-Bed 'quiet gen'
2007 HitchHiker II 32.5 UKTG 2000W Xantex Inverter
US NAVY------USS Decatur DDG31
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
โOct-04-2019 04:52 PM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
โOct-04-2019 03:22 PM
way2roll wrote:er78mph wrote:
I definitely have gas, I bled the system, and it's an Atwood water heater. I'm just sticking a log lighter when I hear the gas and it stays lit for a few seconds and then turns off.
Sounds like the air mixture sleeve or the thermocouple/flame sensor. Can you slide the perforated sleeve to let more or less air in? Too much air and it will blow itself out, too little and the flame won't be strong enough.
Does the stove top light and stay on?
There is also the possibility you have a clog or something in the flame port. I used to get stink bugs in mine I would have to pull them out with tweezers. Mud daubers will clog them too.
Insects clogging things up is why I bought this screen for my water heater, and these screens for the fridge, and these for the furnace. Seemed like cheap insurance to just avoid the problem. Took about 30 minutes to install all 3 sets.
2015 GMC 1500 Sierra 4x4 5.3 3.42 full bed
Equalizer 10k WDH
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
โOct-04-2019 02:18 PM
er78mph wrote:
I definitely have gas, I bled the system, and it's an Atwood water heater. I'm just sticking a log lighter when I hear the gas and it stays lit for a few seconds and then turns off.
Sounds like the air mixture sleeve or the thermocouple/flame sensor. Can you slide the perforated sleeve to let more or less air in? Too much air and it will blow itself out, too little and the flame won't be strong enough.
Does the stove top light and stay on?
There is also the possibility you have a clog or something in the flame port. I used to get stink bugs in mine I would have to pull them out with tweezers. Mud daubers will clog them too.
Jeff - 2023 FR Sunseeker 2400B MBS
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
โOct-04-2019 02:13 PM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
โOct-04-2019 01:32 PM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
โOct-04-2019 01:03 PM
The thermocouple senses the flame and converts it to millivolts to keep the solenoid valve open. If no flame, the valve closes. It's a safety feature to prevent gas from flowing without a flame. If there is a flame but it turns off anyway, the thermocouple could be bad.
But before all that, check to see if your gas is turned on at the tank. Then check your stove to see if it will light and burn. Could also be air in the line and it needs to bleed. Also check to see if you have LP in your tank and it's not empty. But they close the tanks to fill them and often forget to open them back up.
Jeff - 2023 FR Sunseeker 2400B MBS