naturist wrote:
My two generators, a 5500 watt Generac open frame and an 1800 watt ETQ inverter generator both have ground lugs and both say to ground them for safety sake. I seldom do this, and my take on it is hardly anyone else ever does it. But I'll bet that doing so would also solve the issue.
The Generac is for home use, and I drove an extra 8 foot ground rod into the ground next to where that generator would sit when using it to power the house in the event of an outage. But I note that one can as easily get a good ground the old fashioned way: with a battery clamp on a water faucet that has metal pipes.
Grounding it actually won't do anything for the surge guard, as the ground and neutral still would not be bonded. The surge guard has no way of knowing if the ground wire is actually at earth potential as it has nothing to reference its voltage to in an absolute sense. All it can do is look at the voltages between the earth, neutral, and hot wires, and see if they make sense. If the ground is not within a couple of volts of the neutral, it surmises it's either an open ground or (if it is within a couple volts of the hot wire) that the polarity is reversed.
Putting in a bonding plug will make the surge guard think everything is A-OK, whether the ground lug is earthed or not, since it will keep the ground wire voltage from floating arbitrarily.