Forum Discussion
westend
Jun 02, 2015Explorer
You should have a full path between the circuit breakers and the neutral bus. While UNPOWERED (remove shore connection), place a jumper wire in a faulty receptacle and check for continuity between the breaker's output terminal and the neutral bus in the load center. Make sure you have nothing else plugged into any receptacles that would store power in a capacitor. Check with a meter for lack of power, first. You should have continuity between the kitchen receptacle's breaker and the neutral bus with the jumper wire at the receptacle as you know this is operable.
You state "There is another breaker that controls the rest that don't work". Could that breaker be faulty?
You state "There is another breaker that controls the rest that don't work". Could that breaker be faulty?
About Technical Issues
Having RV issues? Connect with others who have been in your shoes.24,190 PostsLatest Activity: Jan 22, 2025