Lantley wrote:Dutch_12078 wrote:
Running the second A/C in our previous 30 amp coach on a separate 20 amp cord to the park utility outlet when needed was a simple low cost conversion process. We haven't needed it yet in our current 50 amp coach, but I could easily do a similar conversion if that changes. The only parts involved were a 4x4" junction box extender, a 20 amp male/female plug pair, and some short lengths of wire. A 12ga extension cord connects the setup to the park box. Total cost about $20. Of course if the 20 amp breaker was slaved off the 30 amp breaker, then that was an issue...
Connecting it to a 50 amp circuit is not quite as simple as using a 30 amp circuit.
Were you able to run both A/C's on a single 30 amp circuit. Most people can't or it is hit or miss.
โFeb-16-2018 09:59 AM
Dutch_12078 wrote:
Running the second A/C in our previous 30 amp coach on a separate 20 amp cord to the park utility outlet when needed was a simple low cost conversion process. We haven't needed it yet in our current 50 amp coach, but I could easily do a similar conversion if that changes. The only parts involved were a 4x4" junction box extender, a 20 amp male/female plug pair, and some short lengths of wire. A 12ga extension cord connects the setup to the park box. Total cost about $20. Of course if the 20 amp breaker was slaved off the 30 amp breaker, then that was an issue...
โFeb-16-2018 09:42 AM
โFeb-16-2018 09:36 AM
โFeb-16-2018 09:08 AM
BB_TX wrote:Bobbo wrote:BB_TX wrote:Bobbo wrote:
...........
In this case, there is no 50 amp neutral. The 30 amp neutral definitely can be overloaded, if the 30 amp and 20 amp outlets are not fed from the same main breaker, but are still on the same leg.
.............
Actually there is a 50 amp neutral all the way from the RV load center to the end of the 50 amp cord where it would plug into the adapter. Then the neutral splits into a 30 amp neutral to the 30 amp plug and a 20 amp neutral to the 20 amp plug. And those two neutrals would connect inside the pedestal.
There is no 50 amp neutral from the pedestal to the main box feeding it. That 30 amp neutral can be overloaded too.
If the pedastal has both a 30 amp and a 20 amp outlet then the neutral from the pedastal to the primary source should be capable of carrying the current for both outlets, or the contractor should have his license revoked.
โFeb-16-2018 08:49 AM
Bobbo wrote:BB_TX wrote:Bobbo wrote:
...........
In this case, there is no 50 amp neutral. The 30 amp neutral definitely can be overloaded, if the 30 amp and 20 amp outlets are not fed from the same main breaker, but are still on the same leg.
.............
Actually there is a 50 amp neutral all the way from the RV load center to the end of the 50 amp cord where it would plug into the adapter. Then the neutral splits into a 30 amp neutral to the 30 amp plug and a 20 amp neutral to the 20 amp plug. And those two neutrals would connect inside the pedestal.
There is no 50 amp neutral from the pedestal to the main box feeding it. That 30 amp neutral can be overloaded too.
โFeb-16-2018 08:48 AM
Bud
USAF Retired
Pace Arrow
โFeb-16-2018 07:31 AM
โFeb-16-2018 07:23 AM
j-d wrote:
I've worked on 50A campground pedestals, but I didn't notice if the 30A and 20A receptacles were on opposite legs of the 50.
โFeb-16-2018 06:47 AM
Bobbo wrote:BB_TX wrote:Bobbo wrote:
...........
In this case, there is no 50 amp neutral. The 30 amp neutral definitely can be overloaded, if the 30 amp and 20 amp outlets are not fed from the same main breaker, but are still on the same leg.
.............
Actually there is a 50 amp neutral all the way from the RV load center to the end of the 50 amp cord where it would plug into the adapter. Then the neutral splits into a 30 amp neutral to the 30 amp plug and a 20 amp neutral to the 20 amp plug. And those two neutrals would connect inside the pedestal.
There is no 50 amp neutral from the pedestal to the main box feeding it. That 30 amp neutral can be overloaded too.
โFeb-16-2018 06:38 AM
BB_TX wrote:Bobbo wrote:
...........
In this case, there is no 50 amp neutral. The 30 amp neutral definitely can be overloaded, if the 30 amp and 20 amp outlets are not fed from the same main breaker, but are still on the same leg.
.............
Actually there is a 50 amp neutral all the way from the RV load center to the end of the 50 amp cord where it would plug into the adapter. Then the neutral splits into a 30 amp neutral to the 30 amp plug and a 20 amp neutral to the 20 amp plug. And those two neutrals would connect inside the pedestal.
โFeb-16-2018 06:33 AM
Bobbo wrote:
...........
In this case, there is no 50 amp neutral. The 30 amp neutral definitely can be overloaded, if the 30 amp and 20 amp outlets are not fed from the same main breaker, but are still on the same leg.
.............
โFeb-16-2018 06:23 AM
CA Traveler wrote:enblethen wrote:Split phase is not needed for the 30+20 amp cheater cord connection as the 50A RV neutral cannot be overloaded.
The two circuits must be on different phases of the electrical source.
You could argue that the cheater cord connected to 30+30 amp (which I've done) could overload the 50A rated neutral if the connection is not split phase.