Jerry, that is my thinking since they do not know the condition from the flood. They do not have any way to high pot test the wiring. Trying to get the state park to get an electrician out to check it.
Ken
That's a good idea to have electrician come out. Make sure he understands fully what is going on.
Testing the pedestal voltage under load is the best way.
Another is to completely disconnect that branch circuit from the main panel then OHM out all wires involved. Hi pot would be best. Should be no continuity between the 4 conductors.
keep us posted.
Good thing you had EMS. I use the same one too.
My neighbor had some serious damage once. He didn't have one.
Jerry
Ps. I've troubleshot and repaired underground problems in the past.
You never know what you might find.