wa8yxm wrote:I am Yu wrote:
OK, it has a fan capacitor, a run cap, and a start cap. I only need to worry about the fan cap, right? (I can hear the compressor coming on.)
Fan cap is marked 7.5 microfarads +/- 10%. Measuring with a Fluke meter gives 6.51 microfarads. Does this mean it's bad... bad enough to cause the motor to lock up?
The fluke meter reading means nothing.. A capacitor can test out good on the fluke at say 9 volts peak (or less) and still be toast at 120 volts.
โApr-26-2014 05:27 AM
I am Yu wrote:
OK, it has a fan capacitor, a run cap, and a start cap. I only need to worry about the fan cap, right? (I can hear the compressor coming on.)
Fan cap is marked 7.5 microfarads +/- 10%. Measuring with a Fluke meter gives 6.51 microfarads. Does this mean it's bad... bad enough to cause the motor to lock up?
โApr-25-2014 10:40 PM
โApr-25-2014 03:42 PM
Altern wrote:
You have a Fluke that measures capacitance? What model number is it?
Most multi-meters are not capable of this. If so, it must have cost a bunch $$$.