pianotuna wrote:
My controller, alas, does not do diversion loads. So if the battery bank is bursting full, I turn on the electric water heater for 15 minutes. That causes the panels to work hard. *grin*
โAug-01-2016 08:32 PM
pianotuna wrote:
Hi grizzzman,
From the owner's manual
"dump loads and consume power from the battery bank to prevent the battery bank from being overcharged by the renewable energy source(s) (e.g.wind turbine, hydro, and solar).
7. Connect a cable from the controllerโs other terminal marked COMMON NEGATIVES to the negative terminal of your DC diversion load. This is the black wire marked โ7โ in Figure 3 below.
8.Connect a cable from the controllerโs terminal marked PV+/LOAD+ to the positive terminal of the DC diversion load. This is the red wire marked โ8โ in Figure 3 below."grizzzman wrote:
C35, C40 and C60 charge controllers can be used as a charge, diversion, or load controller.
"Or" you would need to buy two for charge and diversion.
โAug-01-2016 08:01 PM
grizzzman wrote:
C35, C40 and C60 charge controllers can be used as a charge, diversion, or load controller.
"Or" you would need to buy two for charge and diversion.
โAug-01-2016 06:49 PM
pianotuna wrote:
Hi Almot,
I said good--not expensive. The venerable Xantrex 35 amp PWM 12/24 volt controller does diversion loads and it is $99 bucks on Amazon. It has adjustable voltage set points and provision for a battery bank temperature sensor.
I think MrWizard may be using one.
โAug-01-2016 06:17 PM
โAug-01-2016 06:00 PM
Joel_T wrote:
with a big enough load all of the solar panels amp output would make it to the battery,
โAug-01-2016 01:41 PM
โAug-01-2016 01:36 PM
pianotuna wrote:
Hi Joel,
You may send more amps post controller--but they will be consumed by the load you have placed on the electrical system. So no extra amps will go into the battery. In fact the load may be draining your battery.
Some (good) PWM controllers come with a diversion load feature so that once the battery bank is full the "extra" energy can be sent to (for example) a 12 volt element for the water heater.
โAug-01-2016 01:33 PM
โAug-01-2016 12:58 PM
โAug-01-2016 12:41 PM
Almot wrote:Joel_T wrote:
I'd never thought of getting a big enough load on the batteries to make sure the controller allowed the max amps from the panels out to the batteries.
You won't get more amps to the batteries.
โAug-01-2016 11:50 AM
Joel_T wrote:
I'd never thought of getting a big enough load on the batteries to make sure the controller allowed the max amps from the panels out to the batteries.