Forum Discussion
joebedford
May 21, 2015Nomad II
wnjj wrote:I was about to do the dumb a** thing and post "No, you're wrong" but I decided to confuse the issue with the facts by checking Leviton's instructions. You're more right than me but I was a little bit right. :)joebedford wrote:
AFAIK a GFCI receptacle works equally well in any location on the circuit i.e. it DOESN'T have to be first in the circuit.
The GFCI receptacle itself will work fine, but to protect other receptacles, they must be wired downstream of it.
The GFCI receptacle does not have to be wired first but it will only protect itself and receptacles downstream (i.e. on its load side).